A plain-English map of how electromagnetic locks (maglocks), electric strikes, lockboxes / emergency door releases, and fire-exit (egress) rules fit together in Australia. It is written for homeowners, small businesses and installers. It is a companion to who needs a licence to install alarms, CCTV or access control and to Australian electrical compliance for smart-home work.
It is not legal advice and not compliance advice. It is not a substitute for the National Construction Code, a registered certifier or building surveyor, a fire-services contractor, or the fire-safety schedule for a particular building. If a fact matters for a real door, read the current official NCC clause and the rules that apply in that state or territory, or get the people who will certify the building to tell you what that door must do. Do not treat a forum post, a product brochure, or a “it unlocked in the software†test as a sign-off.
Complexity
Reading: beginner to intermediate. Designing or certifying a required exit is professional work.
1. Fail-safe and fail-secure: what happens when the power dies
Two labels matter more than the brand on the lock:
- Fail-safe (often called fail-unlocked) — when power is removed, the lock releases. A typical maglock is fail-safe: it is a magnet that holds the door only while it is energised. Many “fail-safe†electric strikes behave the same way. On a required exit, that is usually the point: a power cut, a fire-trip that cuts power, or a smashed emergency release should leave the door openable.
- Fail-secure (often called fail-locked) — when power is removed, the lock stays locked. Some electric strikes and motorised locks are built this way so a blackout does not leave the door unlocked. That can be appropriate on a door that is not relied on for escape, but it is a serious trap on a door in a required exit or in the path of travel to one, unless people can still open it from the egress side by a mechanical latch that does not need power or a key.
2. Which NCC edition applies, and what D3D26 actually says
The National Construction Code is published by the ABCB, but each state and territory adopts it on its own date, sometimes with local variations. The clause number for “Operation of latch†is D3D26 in both NCC 2022 Volume One and NCC 2025 Volume One. The official ABCB guidance on D3D26 is the plain-English commentary; it is guidance, not a substitute for the clause.
As at 22 November 2026, the ABCB adoption table and NSW’s official NCC page say:
- NCC 2025 was published on 1 May 2026.
- Victoria, the ACT and Western Australia adopted NCC 2025 on 1 May 2026 (WA also has a 12-month transition — confirm which edition applies to a given job).
- NSW, Queensland and South Australia (BCA) adopt NCC 2025 on 1 May 2027. NSW currently applies NCC 2022 Amendment 2 (from 29 July 2025).
- Tasmania has a published adoption date of 1 May 2027, with a temporary adoption in early May 2026 and a transition period from 5 June 2026 to 1 May 2027. Confirm the edition that applies to the particular building work with the Tasmanian regulator.
- Northern Territory has not adopted NCC 2025. Check NT.GOV.AU / the NT building regulator for the edition in force.
D3D26 applies to a door that is in a required exit, forming part of a required exit, or in the path of travel to a required exit. The ABCB guide’s examples are an external doorway leading from the building, a door leading to or within a fire-isolated exit, and a door in the path of travel to a required exit. In outline, D3D26(1) requires that such a door must be readily openable without a key from the side that faces a person seeking egress, by either:
- a single hand downward action on a single device located between 900 mm and 1.1 m from the floor (and, if it serves an area required to be accessible by Part D4, the handle must be such that a hand that cannot grip will not slip, with a clearance between the handle and the back plate or door face at the centre grip of not less than 35 mm and not more than 45 mm); or
- a single hand pushing action on a single device located between 900 mm and 1.2 m from the floor.
If the push-type device is not on the door leaf itself, D3D26(2) adds rules for the location of manual controls to power-operated doors, and requires braille and tactile signage complying with S15C3 and S15C6 to identify the device.
Related Deemed-to-Satisfy clauses in the same Part, in outline only:
- D3D24 includes a rule that a power-operated door in a path of travel to a required exit must be able to be opened manually under a force of not more than 110 N if the power source malfunctions or fails (with a stated exception for certain Class 9a patient-care doors).
- D3D25 deals with swinging doors in a required exit, including that they must generally swing in the direction of egress, with listed exceptions.
- D3D27 deals with re-entry from fire-isolated exits (doors must not be locked from the inside in listed building classes, with a fail-safe fire-alarm unlock pathway and signage or intercommunication options).
3. When an electronically locked door is allowed
D3D26(3) lists situations where the usual “single-hand, no-key†rules in (1) and (2) do not apply. The two that come up most often around access control are:
D3D26(3)(d) — the fire / sprinkler fail-safe exemption
The usual latch rules do not apply to a door that is fitted with a fail-safe device which automatically unlocks the door upon the activation of any sprinkler system (other than an FPAA101D system) complying with Specification 17, or smoke, or any other detector system deemed suitable in accordance with AS 1670.1 installed throughout the building, and is readily openable when unlocked.
The official ABCB guide says the appropriate authority must be satisfied that the device is genuinely “fail-safe†and that, although power failure is not specifically mentioned in D3D26(3)(d), this would include during power failures; and that in an emergency, access to exits will be enabled immediately, with effectively no time delay.
That is the clause people mean when they talk about a “fire trip†on a maglock. A lockbox, a green emergency button, or a request-to-exit (REX) input that only asks the access-control software to unlock is not, on its own, that automatic unlock.
D3D26(3)(c) and (4) — special security doors
A narrower pathway exists for doors that serve Australian Government Security Zones 4 or 5, or the secure parts of a bank, detention centre, mental health facility, early childhood centre or the like, and that also comply with D3D26(4). Those doors must be able to be immediately unlocked either:
- by operating a fail-safe control switch, not contained within a protective enclosure, to actuate a device to unlock the door; or
- by hand, by a person or persons specifically nominated by the owner, properly instructed, and available at all times when the building is lawfully occupied.
There are other (3) exceptions (vaults and strong-rooms, some sole-occupancy unit entry doors, small SOUs in Class 5–8 buildings of not more than 200 m², spaces inaccessible whenever the door is locked, and a limited Class 9a/9c two-leaf-door case). Those are not a general “shopfront after hours†exemption. D3D26(5) also tightens the rule for many Class 9b rooms or storeys holding more than 100 people (a single-hand pushing action, such as a panic bar). Read the clause and any state variation before you use any of these.
4. Lockboxes, break-glass units and green emergency door releases
These are manual devices, usually mounted on the egress side of the door, that a person can use to release an electric lock:
- a green emergency door release (often a break-glass or resettable call-point style unit)
- a lockbox with a switch inside (sometimes used so the switch is less obvious or less easy to bump)
- older “break-glass†points that physically interrupt the lock circuit when the glass is broken
The honest limit: a lockbox, a break-glass unit, or any other manual release is not on its own a substitute for the automatic fire-alarm or sprinkler unlock that D3D26(3)(d) requires, where that exemption is the reason the door is electrically locked. A person who has already been affected by smoke should not have to find a box, open it, or break a pane as the only way out. And if the door is on the D3D26(3)(c)/(4)(a) pathway, a switch inside a protective enclosure is the opposite of what the clause describes.
5. A wiring principle, without a diagram
If the lock is fail-safe, it holds only while it is powered. A release that is actually fail-safe should break that power directly — a hardwired interruption in the lock’s supply — so that:
- pressing the emergency release drops the lock even if the access-control software has crashed
- a fire-trip or sprinkler interface drops the lock even if the network, the controller, or a “unlock†command never arrives
- a power failure drops the lock, in line with the ABCB guide’s reading of “genuinely fail-safeâ€
6. Fire doors are not ordinary doors
If the door is a required fire door (or smoke door), the lock is part of a tested doorset, not a separate accessory you can swap at will. The ABCB D3D26 guide states that required fire doors must be tested as a complete unit, including the frame and furniture, and that the test of a fire door in an exit includes the opening devices used to comply with D3D26.
Fire and Rescue NSW (position statement, December 2024) requires fire doors to remain functional — openable and closeable — for the duration of a fire, so occupants can leave and firefighters can intervene. FRNSW cites AS 1905.1:2015 on hardware functioning so that the door leaf is self-latching, and warns against supplementary fire-activated retaining devices that can render the door inoperable once they operate.
Do not fit a maglock, drill a fire door, change the closer or latch, or add a lockbox to a fire door unless the hardware is compatible with the certified doorset and the people responsible for the fire-door certification have agreed. A security upgrade that stops a fire door self-latching, or that holds it in a way the tested design did not allow, can undo the door’s fire rating and its egress function at the same time.
7. Standards — only as far as official sources take them
Australian Standards are generally paywalled. This thread does not quote their clauses from memory and does not pretend to be a substitute for the current standard.
- AS 1670.1 — named in D3D26(3)(d) as the reference for a detector system “deemed suitable†and installed throughout the building, as an alternative or companion to a complying sprinkler system.
- AS 1428.1 — named in the ABCB D3D26 guide as the access-and-mobility standard with which the specified handle heights are consistent.
- AS 1905.1 — the fire-resistant doorset standard cited by FRNSW in its fire-door position statement. Installation and any later hardware change need to stay within a compliant, certified doorset.
- AS 1851 — the routine servicing standard for fire protection systems. South Australia’s Metropolitan Fire Service officially points to AS 1851, together with Ministerial Building Standard 002, for ongoing ESP maintenance. Other jurisdictions may also call it up; check the local maintenance rule rather than assuming it.
- AS 4145 (locksets) is an industry lock-hardware standard. It was not found cited in D3D26 itself, and this thread does not treat it as fire-door or egress certification.
No single trade “owns†a required-exit door. In practice you should expect:
- a registered certifier or building surveyor (the appropriate authority for the NCC and the occupancy / building approval) to say whether the door is in a required exit or path of travel, which clause pathway applies, and whether the design is acceptable
- a fire-services contractor to design and commission any fire-detection or sprinkler interface (AS 1670.1 / the building’s fire-safety system), and to involve an accredited fire-safety practitioner where the local rules require one
- a licensed security installer for the access-control and electric-locking work, where that work is a licensed security activity — see t=251
- a licensed electrician for electrical wiring work, with the local compliance certificate — see t=239
- NSW — Annual Fire Safety Statement (AFSS). Under the Environmental Planning and Assessment (Development Certification and Fire Safety) Regulation 2021, the owner of a building with a fire safety schedule must issue an annual fire safety statement. NSW Planning states that an accredited practitioner (fire safety) must have assessed the essential fire safety measures and inspected the exit systems. A copy goes to the local council and to Fire and Rescue NSW, and the statement and current schedule must be displayed in the building. Official starting points: NSW Planning: fire safety certification.
- Victoria — Essential Safety Measures (ESM). The Building and Plumbing Commission / VBA guide says owners of buildings other than a house or outbuilding must maintain essential safety measures so they operate satisfactorily, and must prepare an annual essential safety measures report. The published list includes exit doors, fire curtains and doors, paths of travel to exits, and fire detection and alarm systems, among others. Occupiers must keep exits and paths of travel readily accessible, functional and clear. Records must be kept and produced on request.
- Queensland — occupier’s statement (QDC MP 6.1). Business Queensland states that QDC MP 6.1 applies to Class 1b and Class 2–9 buildings (not Class 1a or Class 10). The occupier (or the owner if there is no occupier) must maintain prescribed fire safety installations and give a yearly occupier’s statement to the Commissioner of the Queensland Fire Department.
- South Australia — Essential Safety Provisions (ESP), Form 3. The SA Metropolitan Fire Service and PlanSA state that ESPs must be maintained (MFS points to AS 1851 and Ministerial Building Standard 002). Unless exempted, the owner must give annual maintenance verification to the council on Form 3, not later than 60 business days after the end of each calendar year (Planning, Development and Infrastructure (General) Regulations 2017, regulation 94(11)).
- WA, Tasmania, the ACT and the NT also impose maintenance obligations on building owners or occupiers, but this thread does not invent a statement title or lodgement date that was not confirmed on an official page fetched for this research. Ask the local building regulator, council or fire authority what must be inspected, recorded and lodged for that building.
The NCC clause number to look up is still D3D26. The edition, the adoption date and any state variation are what change. Use the ABCB adoption table and the local variations tab, then the local maintenance regime in section 8.
- NSW — currently NCC 2022 Amendment 2, until NCC 2025 on 1 May 2027. Read NSW D3D26(5) and (6) for certain Class 9b / entertainment-venue doors. AFSS for existing buildings with a fire safety schedule.
- Victoria — NCC 2025 from 1 May 2026, including the published VIC D3D26(1) variation for some early-childhood-centre exit doors. Annual ESM report. Building surveyor / BPC (formerly often referred to as the VBA) and the relevant fire authority have enforcement roles under the Building Regulations 2018.
- Queensland — NCC 2022 remains in force until NCC 2025 starts on 1 May 2027 (official Business Queensland / QBCC position). Yearly occupier’s statement under QDC MP 6.1.
- Western Australia — NCC 2025 adopted 1 May 2026, with a 12-month transition. Confirm the edition for the job with the WA building regulator. Check local ESM / maintenance rules with that regulator; they are not restated here.
- South Australia — BCA (Volumes One and Two) adopts NCC 2025 on 1 May 2027 (PCA already adopted 1 May 2026). Annual Form 3 ESP verification to council.
- Tasmania — confirm the applicable NCC edition during the published transition through to 1 May 2027. Check CBOS / the Director of Building Control for maintenance obligations.
- ACT — NCC 2025 adopted 1 May 2026, with a 12-month transition. Check Access Canberra / ACT planning for maintenance rules.
- Northern Territory — NCC 2025 not adopted. Confirm the in-force edition and any maintenance rules with Licensing NT / the NT building regulator.
This is a planning list for a typical small commercial door that will have a reader, a maglock, a request-to-exit button, a manual release, and a fire trip. It is not a design, and it is not enough on a required fire door or a required exit without the certifier’s agreement.
Before anyone orders hardware:
- Has a certifier or building surveyor said whether this door is in a required exit, forms part of one, or is in the path of travel to one? If yes, D3D26 is in play (subject to the building class and any applicable exception).
- Which NCC edition and which state variations apply to this building or this alteration?
- Is the door a fire door or smoke door? If yes, stop and use only hardware that belongs on that certified doorset.
- Is the lock fail-safe, and does it remain readily openable from the egress side without a key when it is unlocked or unpowered?
- Will the fire detection or sprinkler system automatically unlock the door, if D3D26(3)(d) is the pathway being used? Who is designing and commissioning that interface?
- Is there a local manual release on the egress side, mounted at a usable height, that breaks lock power directly? If you are on the (3)(c)/(4)(a) pathway, it must not be inside a protective enclosure.
- Is there a mechanical or fail-safe way out if the access controller, the reader, or the building network is dead?
- Have the security installer, the electrician and the fire-services contractor been identified, and are they actually licensed for their part of the work?
- Will the lock, the fire trip and the door itself appear on the fire safety schedule / essential safety measures list, and who will inspect them each year?
- Fitting a fail-secure lock, or a maglock with a hidden battery that keeps the door locked, on a door people must use to escape.
- Treating a lockbox or green break-glass as the fire trip.
- A fire “unlock†that exists only as a software input, a delayed command, or something a controller can ignore.
- A REX button that requests an unlock the software never grants if the door is “secured†or the network is down.
- Mounting the release too high, too low, behind a plant, or only on the secure side.
- Putting the only manual switch inside a locked or glazed lockbox on a door that is relying on D3D26(4)(a).
- Drilling or re-hanging a fire door, or adding a maglock, without certified hardware and sign-off.
- Forgetting that a power-operated door may also have to be openable by hand under 110 N if the power fails (D3D24).
- Assuming a Class 1a house rule applies to a shop, office, boarding house or mixed-use building — or the reverse.
- Leaving the owner with no paperwork for the annual fire safety / essential safety measures statement.
NCC 2025 Volume One, Part D3 (includes D3D26)
NCC 2022 Volume One, Part D3 (includes D3D26)
ABCB guide: D3D26 Operation of latch
NCC 2025 state and territory adoption dates
ABCB: building classifications
NSW: how to comply with the NCC
NSW Planning: fire safety certification (AFSS)
Fire and Rescue NSW: lodge a fire safety statement
FRNSW: fire doors and fire-activated retaining devices (PDF)
Victoria BPC/VBA: essential safety measures
Business Queensland: fire safety installations and occupier’s statement
Business Queensland: delayed adoption of NCC 2025
PlanSA: Form 3 ESP maintenance certificate
SA MFS: maintenance of fire safety systems
Just Smart Homes t=251: security licensing
Just Smart Homes t=239: electrical compliance
This is not legal or compliance advice. NCC editions, state variations, and fire-safety maintenance rules change. Check the official in-force NCC clause and the regulator for the state or territory where the building sits, and the fire safety schedule or essential safety measures list for that building, before you rely on any point in this thread. Researched from official documentation on 22 November 2026 (Australia/Sydney). Please correct anything that has moved on.